  • #4285
    Kimberranch
    Participant

    Hi, i just got the bhyve 12 station and started to unhook my old toro controller and noticed that there is a wire in the 12v and 24v ports on the toro and the bhyve dosnt have a 12v port, what do i do?

    Any help is greatly appreciated.

    Thanks

    Spread the love!
    #4331
    Ryan
    Participant

    Hello Kimberranch, You’ll want to check and make sure whether the 24V ports were for a power source or a rain sensor on your old Toro timer. We have 24VAC out terminals for a pump start relay connection. If they are just for a power source then you wouldn’t use them, because the transformer is already built into the timer. As for the 12V port you will need to contact Toro to find out what it was for exactly, and then we can assist you after that. Please let us know if you have any further questions.