Community Home › Community › B-hyve › Underground › Station faults — system cannot turn water off › Reply To: Station faults — system cannot turn water off
It looks like your valves may have 12 Volt Latching DC solenoids instead of 24 Volt AC standard solenoids. Notice how the side of your old timer says Output: 11 Volts DC. I don’t think the B-Hyve timer will work with that style of solenoid and can only use 24 Volt AC solenoids. You could probably change yours to be 12VAC by replacing just the solenoid on each valve. The ‘Fault’ error is probably from your solenoids drawing too much current from the timer.
This solenoid would probably work. I’m sure it would work with the timer but I don’t know what valves you have so I would buy one and test it first. I think the link I wanted to post is getting blocked. Just search for this part below.
Hunter – 606800 – Replacement 24V Solenoid