Community Home Community B-hyve B-Hyve outputs 28vac to all zones when only one zone turned on.

Viewing 1 post (of 1 total)
  • Author
    Posts
  • #82074
    shosky
    Participant
    Points: 1
    Up
    1
    Down
    ::

    Installed a new B-Hyve 12 zone system. When I attempt to test one zone at a time, I am seeing 28vac on that zone but all other zones also read 28vac even and none of the zones will activate. Any ideas on what’s going on? Bad unit? Wiring issue cause this? Verified common is correct and terminated properly.

Viewing 1 post (of 1 total)
  • You must be logged in to reply to this topic.